[staff-physics-and-astronomy-HL-UHD-UD] Update meeting 06 May 2025 Information meeting on VO lab climate systems / Technische info meeting klimaat VO-labs natuurkunde ( Beeldplaatjes, Short Update & Minutes)

Beta NAT Secretariaat natsecr.beta at vu.nl
Tue May 6 16:40:39 CEST 2025


Dear all,



On behalf of Robert van Leijenhorst and Desiree Denie the following documents have been added

to teams NS-All Employees,  08. VU Onderzoeksgebouw - Research Building you can find the folder [?Folder icon]  Climate-related reports Research Building VU<https://vunl.sharepoint.com/:f:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU?csf=1&web=1&e=YtDZHL> :



[?docx icon] 2025-05-06 - Aantekeningen Information meeting on VO lab climate systems _ Technische info meeting klimaat VO-labs natuurkunde.docx<https://vunl.sharepoint.com/:w:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU/2025-05-06%20-%20Aantekeningen%20Information%20meeting%20on%20VO%20lab%20climate%20systems%20_%20Technische%20info%20meeting%20klimaat%20VO-labs%20natuurkunde.docx?d=w75c34333958c403592e4ce0b68b02537&csf=1&web=1&e=WBoLKD>

[?log icon] 2025-05-06 Feedback meeting May 6 ( Dutch).log<https://vunl.sharepoint.com/:u:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU/2025-05-06%20Feedback%20meeting%20May%206%20(%20Dutch).log?csf=1&web=1&e=2vlK5f>

Due to time constraints, the status of the reports will not be shared today, but next Thursday.
A new meeting will be scheduled.


From: _list_senior-staff-physics-and-astronomy-bounces <senior-staff-physics-and-astronomy-bounces at listserver.vu.nl> On Behalf Of Beta NAT Secretariaat

Sent: Friday, 25 April 2025 13:02
To: Heller, I. (iddo) <i.heller at vu.nl>; Eikema, K.S.E. (KSE) <k.s.e.eikema at vu.nl>; Dahlberg, J.D. (Jordi) <j.dahlberg at vu.nl>; Slaman, M.J. (Martin) <m.j.slaman at vu.nl>; Stoop, A.H. (Albert) <a.h.stoop at vu.nl>; Sasbrink, G.D.J. (Bart) <g.d.j.sasbrink at vu.nl>; Dalebout, T.J. (Tim) <t.j.dalebout at vu.nl>; Biebricher, A.S. (Andreas) <a.s.biebricher at vu.nl>; Marzin, M. (Manuel) <m.marzin at vu.nl>; Slijper, J.V. (Joanne) <j.v.slijper at vu.nl>; Kortekaas, R. (R) <r.kortekaas at vu.nl>; _list_senior-staff-physics-and-astronomy <senior-staff-physics-and-astronomy at listserver.vu.nl>; Rojo, J. (Juan) <j.rojo at vu.nl>; Croce, R. (Roberta) <r.croce at vu.nl>; Chukhutsina, V.U. (Volha) <v.u.chukhutsina at vu.nl>; Kennis, J.T.M. (John) <j.t.m.kennis at vu.nl>; Ramanan, C. (Charusheela) <c.ramanan at vu.nl>; Groot, M.L. (ML) <m.l.groot at vu.nl>; Blankesteijn, M.L. (Marie Louise) <m.l.blankesteijn at vu.nl>; Do, T.N. (Thanh Nhut) <t.n.do at vu.nl>; Ariese, F. (Freek) <f.ariese at vu.nl>; Dulin, D. (David) <d.dulin at vu.nl>; Peterman, E.J.G. (Erwin) <e.j.g.peterman at vu.nl>; Baldi, A. (Andrea) <a.baldi at vu.nl>; Bethlem, H.L. (HL) <h.l.bethlem at vu.nl>; Fokkema, D.B.R.A. (David) <d.b.r.a.fokkema at vu.nl>; Ubachs, W.M.G. (Wim) <w.m.g.ubachs at vu.nl>; Hocaoglu, M. (Melike) <m.hocaoglu at vu.nl>; Kuik, G.J. (GJ) <g.j.kuik at vu.nl>; Stokkum, I.H.M. van (IHM) <i.h.m.van.stokkum at vu.nl>; Colvin, K.S. (Karin) <k.s.colvin at vu.nl>; Desiree Denie <facilitated_projects at outlook.com>; Heijningen, J.V. van (Joris) <j.v.van.heijningen at vu.nl>; Askes, S.H.C. (Sven) <s.h.c.askes at vu.nl>; Helgert, J. (Johannes) <j.helgert at vu.nl>
Cc: Goossens, P.E. (PE) <p.e.goossens at vu.nl>; Denie, D. (Desiree) <d.denie2 at vu.nl>; Robert van Leijenhorst <robert at endurance-advies.nl>
Subject: [staff-physics-and-astronomy-HL-UHD-UD] Update meeting 22 april 2025 Information meeting on VO lab climate systems / Technische info meeting klimaat VO-labs natuurkunde ( Beeldplaatjes, Short Update & Minutes)

Dear all,

On teams NS-All Employees,  08. VU Onderzoeksgebouw - Research Building you can find the folder [?Folder icon]  Climate-related reports Research Building VU<https://vunl.sharepoint.com/:f:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU?csf=1&web=1&e=YtDZHL> which contains :

2025-04-25         Beeldplaatjes [?Folder icon]  2025-04-25 beeldplaatjes overzicht uit het GBS<https://vunl.sharepoint.com/:f:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU/2025-04-25%20beeldplaatjes%20overzicht%20uit%20het%20GBS?csf=1&web=1&e=ZgYu4P> as shared by Rbert van Leijenhorst today
2025-04-24         Short update on the indoor climate in the VU Research Building  [?docx icon]  2025-04-22 Aantekeningen Information meeting on VO lab climate systems _ Technische info meeting klimaat VO-labs natuurkunde.docx<https://vunl.sharepoint.com/:w:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU/2025-04-22%20Aantekeningen%20Information%20meeting%20on%20VO%20lab%20climate%20systems%20_%20Technische%20info%20meeting%20klimaat%20VO-labs%20natuurkunde.docx?d=w7f711016d95b4b5abd6197ae54466c2d&csf=1&web=1&e=Dhw8YN>
2025-04-22         Minutes 22 april 2025 [?url icon]  2025-04-24 FYI Short update on the indoor climate in the VU Research Building.url<https://vunl.sharepoint.com/:u:/r/sites/BETA-OE-GeneralInformationPhysicsAstronomy/Shared%20Documents/08.%20VU%20Onderzoeksgebouw%20-%20Research%20Building/Climate-related%20reports%20Research%20Building%20VU/2025-04-24%20FYI%20Short%20update%20on%20the%20indoor%20climate%20in%20the%20VU%20Research%20Building.url?csf=1&web=1&e=fBQNae> shared by Desiree Denie ( see also below)


Minutes 22 april 2025
Vanwege de onvrede over de werking van het klimaatsysteem is er een overleg geïnitieerd voor Natuurkunde waarbij de lab-adviseur van de VU een toelichting geeft over het ontwerp van het klimaatsysteem, de uitvoering en een doorkijk naar de problemen.
De meeting start met een visual van de klimaatinstallatie uit het gebouwbeheersysteem en een toelichting op het ontwerp:
·        De buitenconditie wordt in het centrale systeem gereguleerd tot een vaste luchtconditie, op dit moment 16ºC met 7gr/kg vocht.
Daarna wordt de lucht het gebouw doorgevoerd en decentraal in de labs conform het ingestelde temperatuur setpoint nogmaals aangepast door de lokale systemen (vochtigheid kan lokaal niet meer worden bijgesteld).
·        Het ontwerp is ontwikkeld voor extreme buitenomstandigheden (-10ºC en +30ºC).
·        Er zijn 8 luchtbehandelingskasten voor de laboratoria aanwezig in het gebouw die onderdeel zijn van het centrale klimaatsysteem.
·        In de laboratoria zijn meerdere temperatuursensoren geïnstalleerd. Het systeem elimineert de extreme (max en min) waarden en van de overige waarden wordt een gemiddelde genomen als meting voor de temperatuur in de ruimte.
·        De invoertemperatuur vanuit het centrale systeem is op dit moment constant 16 graden. In het oorspronkelijke ontwerp was dit 12 graden maar dit is aangepast omdat de decentrale regelingen de ruimten niet op temperatuur kregen. Dit koste ook heel veel (onnodige) energie. Kjeld vraagt zich af of de temperatuur in de zomer verlaagd zou moeten worden conform oorspronkelijk ontwerp.  Robert stelt dat dit niet nodig is en ook de vochthuishouding dan weer in de war brengt. Daarnaast is dit ook niet energiezuinig omdat je de warme buitenlucht eerst extreem koelt om deze vervolgens weer op te warmen tot 20 graden in de labs. Een gemiddeld life science lab zou voldoende hebben aan een aanvoertemperatuur van 18 graden. Omdat dit gebouw laserruimtes bevat, is gekozen voor een aanvoertemperatuur van 16 graden.
·        De koel- en verwarmingscapaciteit is gebaseerd op het aantal m3 ventilatie in het lab.
·        Daarnaast zijn er berekeningen gemaakt over de hoeveelheid zoninstraling, warmte-isolatie van de gevel, dak etc. Dit heeft geresulteerd in labs met een bepaalde capaciteit koel- en verwarmingscapaciteit.
·        In de laserlabs is naast verwarming ook altijd aanvullende koeling aangebracht.
Tussendoor zijn er vragen van de deelnemers die beantwoord worden:
·        Maximilian vraagt wat de maximale temperatuur is die men als setpoint kan instellen. Antwoord is 24 graden
·        Bart stelt dat hij last heeft van extreem warme ruimtes. In het lab met de klimaatkamers (1A-036 GBS) is een ontwerpfout gemaakt. Hier staat veel apparatuur in en er is geen aanvullende koeling aanwezig. Bart geeft aan dat hij ook problemen heeft met hoge temperaturen in zijn laserlabs (1A-132 en 1A-145). 1A-145 is bekeken op het scherm. Voorzichtige conclusie is dat in deze ruimte de koelklep 100% open gaat, maar er geen koelwater over de batterij loopt. Hierdoor gaat de ventilator 100% en dit produceert veel herrie. Theoretisch zou de gevraagde koelcapaciteit met 50% van het ventilatorvermogen gehaald moeten worden.
·        Kjeld heeft niet het idee dat het ijken van de sensoren tot de oplossing leidt. De zichtlijn van de sensoren is ook problematisch. Deze wijzen nu naar beneden waardoor ze beïnvloed kunnen worden door mensen en lokale labapparatuur.  Hij stelt dat het beter is om ze naar de muren te richten. Daarnaast veronderstelt hij ook dat deze sensoren ongeschikt zijn voor toepassing in de laboratoria. Robert geeft aan dat er een proef wordt gedaan met andere lenzen op de sensoren.
·        Albert stelt voor om een plaat onder de sensor te hangen. Kjeld geeft aan dat hij dit geprobeerd heeft maar dat deze plaat ook de luchthuishouding nadelig beïnvloed.
·        Iddo en Kjeld stellen voor om de waardes van alle sensoren in het bedieningspanelen te tonen zodat men deze sensoren zelf in de gaten kan houden. Dit is helaas technisch niet mogelijk.
·        Maximilian stelt voor om inzicht te krijgen in het systeem en zelf sensoren aan te schaffen die wel werken. Robert gaat na of dit mogelijk is en welke sensoren compatible zijn met het systeem.
De afgelopen maanden zijn er al meerdere verbeteringen doorgevoerd zo zijn:
·        In de hoogbouw is een aanpassing gedaan die het klimaat verbeterd hebben.
·        De aanvoertemperatuur is aangepast
·        Kleppen aangepast
·        Proef: Multiple zones in 1 ruimte teruggebracht naar 1 zone
·        Proef: Sensoren herijkt
·        Men heeft een setting veranderd van de bedieningspanelen en de reactie is veel sneller. Deze oplossing wordt uitgerold over het hele gebouw.
Men had de hoop een structureel probleem te vinden en te kunnen oplossen. Daarna kon de aandacht gericht worden op de dan nog aanwezige lokale problemen. De laboratoria hebben echter veel verschillende klimaat gerelateerde problemen. Voor ieder lab moet daarom worden onderzocht wat het probleem is.
Afspraken:
·        Natuurkunde stelt voor om mee te denken aan de oplossing als zij toegang kunnen krijgen tot de visuals uit het GBS. Robert stelt voor om de leverancier te verzoeken extra capaciteit in te zetten om de lokale problemen te diagnosticeren
o   Robert stuurt screenshot van ieder lab zodat de Natuurkunde collega's mee kunnen denken bij het formuleren van de oplossing. Secretariaat mailt het door.
·        Martin heeft het dringende verzoek om andere sensoren te plaatsen als proef. Robert bespreekt de mogelijkheden met de aannemer
·        Iddo verzoekt om de klimaatproblemen nog niet bij de lijnorganisatie onder te brengen en nog door het projectteam op te laten lossen.
o   Aanvulling: Desiree heeft dit nagevraagd en het blijkt dat de (nieuwe) klimaat gerelateerde meldingen niet door de lijn worden opgepakt maar door het projectteam.
·        Over 2 weken weer een nieuw overleg met update
·        Wekelijks een terugkoppeling per mail met de statusvoortgang.
 -------------------------------------------------------------------------------------------------------
Due to the dissatisfaction with the operation of the climate system, a consultation was initiated for Physics in which the installation advisor from the VU provided an explanation about the design of the climate system, its implementation and an overview of the problems. The meeting starts with a visual of the climate installation from the building management system
The meeting starts with a visual of the climate system from the building management system and an explanation of the design:
·        The outdoor condition is regulated in the central system to a fixed air condition, currently 16ºC with 7gr/kg moisture. The air is then transported through the building and adjusted again decentrally in the labs in accordance with the set temperature set point by the local systems (humidity can no longer be adjusted locally).
·        The design has been developed for extreme (-10 and +30)
·        There are 8 air handling units in the building that are part of the central climate system.
·        Multiple sensors are installed in the laboratories. The system eliminates the extreme (max and min) values and an average of the remaining values is taken as a measurement of the temperature in the room.
·        The inlet temperature from the central system is currently a constant 16 degrees. In the original design this was 12 degrees but this was adjusted because the decentralized controls could not get the rooms up to temperature. This also cost a lot of (unnecessary) energy. Kjeld wonders whether the temperature should be lowered in the summer according to the original design. Robert states that this is not necessary and also disrupts the humidity control. In addition, this is also not energy efficient because you first cool the warm outside air extremely and then heat it up again to 20 degrees in the labs. An average life science lab would have enough with a supply temperature of 18 degrees. Because this building contains laser rooms, a supply temperature of 16 degrees was chosen.
·        The cooling and heating capacity is based on the number of m3 of ventilation in the lab
·        In addition, calculations have been made regarding the amount of solar radiation, thermal insulation of the facade, roof, etc. This has resulted in labs with a certain cooling and heating capacity.
·        There is always additional cooling in the laser labs.

In between there are questions from the participants that are answered:
·        Maximilian asks what the maximum temperature is that can be set as a set point. The answer is 24 degrees
·        Bart states that he is having problems with extremely warm spaces. A design mistake was made in the climate chambers. There is a lot of equipment in here and there is no additional cooling available. Bart states that he also has problems with high temperatures in his laser labs (1A-132 and 1A-145). 1A-145 is viewed on the screen. The cautious conclusion is that in this room the cooling valve opens 100%, but no cooling water runs over the battery. This causes the fan to run at 100% and produces a lot of noise. Theoretically, the required cooling capacity should be achieved with 50% of the fan capacity.
·        Kjeld does not think that calibrating the sensors will lead to the solution. The sensors' line of sight is also problematic. These now point downwards, which means they can be influenced by people and local lab equipment. He states that it is better to point them towards the walls. He also assumes that these sensors are unsuitable for use in laboratories. Robert indicates that a test is being done with other lenses on the sensors.
·        Albert proposes to hang a plate under the sensor. Kjeld indicates that he has tried this, but that this plate also has a negative effect on the air balance.
·        Iddo and Kjeld propose to display the values of all sensors in the control panels so that people can monitor these sensors themselves. Unfortunately, this is not technically possible.
·        Maximilian proposes to gain insight into the system and to purchase sensors that do work. Robert examines whether this is possible and which sensors are compatible with the system.

Several improvements have been made in recent months, including:
·        Adjustments have been made to the high-rise buildings that have improved the climate.
·        Adjusted the supply temperature
·        Valves adjusted
·        Test: Multiple zones in 1 room reduced to 1 zone
·        Test: Sensors recalibrated
·        A setting has been changed on the control panels and the response is much faster. This solution is being rolled out throughout the building.
The hope was that a structural problem would be found and solved. Attention could then be focused on the still existing local problems. However, the labs have many different climate-related problems. The problem must therefore be investigated for each lab.
Appointments:
·        Physics proposes to help think about the solution if they can access the visuals from the GBS. Robert suggests asking the supplier to deploy additional capacity to diagnose local problems
·        Robert sends screenshots of each lab so that his Physics colleagues can help formulate the solution. The secretariat will forward it by email.
·        Martin has an urgent request to install other sensors as a test. Robert discusses the options with the contractor
·        Iddo requests that the climate problems not yet be transferred to the line organization and that they be solved by the project team. Desiree has asked about this and it appears that the (new) climate-related reports are not picked up by the line but by the project team.
·        Another meeting with update in 2 weeks
·        Weekly feedback by email with status progress.


________________________________
Van: Beta NAT Secretariaat <natsecr.beta at vu.nl<mailto:natsecr.beta at vu.nl>>
Verzonden: dinsdag 22 april 2025 09:56
Aan: Heller, I. (iddo) <i.heller at vu.nl<mailto:i.heller at vu.nl>>; Eikema, K.S.E. (KSE) <k.s.e.eikema at vu.nl<mailto:k.s.e.eikema at vu.nl>>; Robert van Leijenhorst <robert at endurance-advies.nl<mailto:robert at endurance-advies.nl>>; Dahlberg, J.D. (Jordi) <j.dahlberg at vu.nl<mailto:j.dahlberg at vu.nl>>; Slaman, M.J. (Martin) <m.j.slaman at vu.nl<mailto:m.j.slaman at vu.nl>>; Stoop, A.H. (Albert) <a.h.stoop at vu.nl<mailto:a.h.stoop at vu.nl>>; Sasbrink, G.D.J. (Bart) <g.d.j.sasbrink at vu.nl<mailto:g.d.j.sasbrink at vu.nl>>; Dalebout, T.J. (Tim) <t.j.dalebout at vu.nl<mailto:t.j.dalebout at vu.nl>>; Biebricher, A.S. (Andreas) <a.s.biebricher at vu.nl<mailto:a.s.biebricher at vu.nl>>; Marzin, M. (Manuel) <m.marzin at vu.nl<mailto:m.marzin at vu.nl>>; Slijper, J.V. (Joanne) <j.v.slijper at vu.nl<mailto:j.v.slijper at vu.nl>>; Kortekaas, R. (R) <r.kortekaas at vu.nl<mailto:r.kortekaas at vu.nl>>; _list_senior-staff-physics-and-astronomy <senior-staff-physics-and-astronomy at listserver.vu.nl<mailto:senior-staff-physics-and-astronomy at listserver.vu.nl>>
CC: Denie, D. (Desiree) <d.denie2 at vu.nl<mailto:d.denie2 at vu.nl>>; Goossens, P.E. (PE) <p.e.goossens at vu.nl<mailto:p.e.goossens at vu.nl>>; Rojo, J. (Juan) <j.rojo at vu.nl<mailto:j.rojo at vu.nl>>; Croce, R. (Roberta) <r.croce at vu.nl<mailto:r.croce at vu.nl>>; Chukhutsina, V.U. (Volha) <v.u.chukhutsina at vu.nl<mailto:v.u.chukhutsina at vu.nl>>; Kennis, J.T.M. (John) <j.t.m.kennis at vu.nl<mailto:j.t.m.kennis at vu.nl>>; Ramanan, C. (Charusheela) <c.ramanan at vu.nl<mailto:c.ramanan at vu.nl>>; Groot, M.L. (ML) <m.l.groot at vu.nl<mailto:m.l.groot at vu.nl>>; Blankesteijn, M.L. (Marie Louise) <m.l.blankesteijn at vu.nl<mailto:m.l.blankesteijn at vu.nl>>; Do, T.N. (Thanh Nhut) <t.n.do at vu.nl<mailto:t.n.do at vu.nl>>; Ariese, F. (Freek) <f.ariese at vu.nl<mailto:f.ariese at vu.nl>>; Dulin, D. (David) <d.dulin at vu.nl<mailto:d.dulin at vu.nl>>; Peterman, E.J.G. (Erwin) <e.j.g.peterman at vu.nl<mailto:e.j.g.peterman at vu.nl>>; Baldi, A. (Andrea) <a.baldi at vu.nl<mailto:a.baldi at vu.nl>>; Bethlem, H.L. (HL) <h.l.bethlem at vu.nl<mailto:h.l.bethlem at vu.nl>>; Fokkema, D.B.R.A. (David) <d.b.r.a.fokkema at vu.nl<mailto:d.b.r.a.fokkema at vu.nl>>; Ubachs, W.M.G. (Wim) <w.m.g.ubachs at vu.nl<mailto:w.m.g.ubachs at vu.nl>>; Hocaoglu, M. (Melike) <m.hocaoglu at vu.nl<mailto:m.hocaoglu at vu.nl>>; Kuik, G.J. (GJ) <g.j.kuik at vu.nl<mailto:g.j.kuik at vu.nl>>; Stokkum, I.H.M. van (IHM) <i.h.m.van.stokkum at vu.nl<mailto:i.h.m.van.stokkum at vu.nl>>; Colvin, K.S. (Karin) <k.s.colvin at vu.nl<mailto:k.s.colvin at vu.nl>>; Desiree Denie <facilitated_projects at outlook.com<mailto:facilitated_projects at outlook.com>>; Heijningen, J.V. van (Joris) <j.v.van.heijningen at vu.nl<mailto:j.v.van.heijningen at vu.nl>>; Askes, S.H.C. (Sven) <s.h.c.askes at vu.nl<mailto:s.h.c.askes at vu.nl>>; Helgert, J. (Johannes) <j.helgert at vu.nl<mailto:j.helgert at vu.nl>>
Onderwerp: Information meeting on VO lab climate systems / Technische info meeting klimaat VO-labs natuurkunde
Wanneer: dinsdag 22 april 2025 10:00-11:30.
Waar: VO-01B001 Vergaderruimte Spectrum 1


Since lab climate and temperature are integral parts of our experimental setups, we have asked the building team to organize a technical information meeting on this topic.

In this meeting, VO lab-climate expert Robert van Leijenhorst will explain the technical implementation, current/encountered problems and solutions of our VO climate and temperature measurement&control systems.

There will be time for Q&A.



NB. This e-mail is sent to physics staff & technicians, feel free to forward to other interested lab members.



Iddo Heller

________________________________________________________________________________

Microsoft Teams Need help?<https://aka.ms/JoinTeamsMeeting?omkt=en-US>

Join the meeting now<https://teams.microsoft.com/l/meetup-join/19%3ameeting_YWM5YmQyYWEtZDczMC00MjIxLWJhOTYtZjFiYTFmODI1YzAz%40thread.v2/0?context=%7b%22Tid%22%3a%22462a9c9c-2da6-4bfb-b318-0f83043fe49b%22%2c%22Oid%22%3a%220da30af3-9b2c-4245-b9eb-116d29b5738b%22%7d>

Meeting ID: 331 147 395 719 9

Passcode: gG2Xv26q

________________________________

Dial in by phone

+31 20 399 0553,,49748627#<tel:+31203990553,,49748627> Netherlands, Amsterdam

Find a local number<https://dialin.teams.microsoft.com/72e2792e-ebd6-4186-b4ce-8864539f4489?id=49748627>

Phone conference ID: 497 486 27#

For organizers: Meeting options<https://teams.microsoft.com/meetingOptions/?organizerId=0da30af3-9b2c-4245-b9eb-116d29b5738b&tenantId=462a9c9c-2da6-4bfb-b318-0f83043fe49b&threadId=19_meeting_YWM5YmQyYWEtZDczMC00MjIxLWJhOTYtZjFiYTFmODI1YzAz@thread.v2&messageId=0&language=en-US> | Reset dial-in PIN<https://dialin.teams.microsoft.com/usp/pstnconferencing>

Je kunt deze vergadering ook bijwonen als je niet over Microsoft Teams beschikt.

Org help<https://support.microsoft.com/en-gb/office/microsoft-teams-for-education-help-079671e6-f0c5-4450-abf6-ccccc18c1fac?ns=msteamsedutr&version=16&ui=en-us&rs=en-gb&ad=gb> | Privacy and security<https://www.vu.nl/nl/index.aspx>

________________________________________________________________________________





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://listserver.vu.nl/pipermail/senior-staff-physics-and-astronomy/attachments/20250506/0587a559/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 210 bytes
Desc: image001.png
URL: <https://listserver.vu.nl/pipermail/senior-staff-physics-and-astronomy/attachments/20250506/0587a559/image001-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 444 bytes
Desc: image002.png
URL: <https://listserver.vu.nl/pipermail/senior-staff-physics-and-astronomy/attachments/20250506/0587a559/image002-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 267 bytes
Desc: image003.png
URL: <https://listserver.vu.nl/pipermail/senior-staff-physics-and-astronomy/attachments/20250506/0587a559/image003-0001.png>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: ATT00001.txt
URL: <https://listserver.vu.nl/pipermail/senior-staff-physics-and-astronomy/attachments/20250506/0587a559/ATT00001-0001.txt>


More information about the Senior-staff-physics-and-astronomy mailing list